How to tune a PID controller? best practice
Step 1: P = Proportional gain
P - Background
- Proportional gain should get you most of the way to the finish line - this is likely the largest win of the 3.
- Proportional looks at how far you are away from the setpoint and applies force in the opposite direction to push you toward setpoint.
P - How to tune the Proportional gain?
- Step 1 Zero out the other gains and focus on tuning the P first.
- Step 2 There is some P gain value above which the loop goes unstable - stay well below that point. Too high proportional gain and you get uncontrollable osscillations.
- Step 3 Slow reaction to stimulus? Increase proportional gain.
- Step 4 You’re done setting the P when you’ve got a steady state offset error. This is expected and fine.
Step 2: I = Integral gain
I - Background
- If you have a steady state offset from the proportional, you fix that with a little bit of integral.
- The integral portion of the control loop looks at how far you are away from setpoint for how long (that extra time component is the key difference between P and I).
- It pushes a little bit if you’re away from setpoint for a little bit of time and pushes ever harder the longer you stay away from setpoint.
I - How to tune:
- Step 5 Start the I at 0 (zero) and bring it up.
- Step 6 You know you’ve overdone the I gain when you get a steady state oscillation.
- Step 7 Often it is typical to end up with something like I=P/20, but your case may of course be different.
Step 3: D = Derivative gain
D - Background
- Derivative gain helps predict future errors.
- It acts as a dampening force, slowing down the system’s response as it approaches the setpoint to minimize overshoot.
- So it’s basically telling your controller how big the lag is between its action and the actual response of the system. A big D means telling your controller there’s a big lag so it can anticipate that.
D - How to tune?
- Step 8 Begin with the D gain set to zero and only adjust it after tuning P and I.
- Step 9 Increase D gain until the loop responds quickly to changes without overshooting the setpoint.
- Step 10 If the system starts to oscillate or becomes too “jittery,” bring down the D gain.
- Step 11 Noise affects the performance of the D gain, so use a filter if necessary to remove high-frequency fluctuations.
Important remarks for practitioners
Theory tells you:
- There’s math you can do to theoretically calculate the gains.
- Most of literature says those of us who tune by feel are dumb and should at least feel bad for doing so.
Practice teaches us:
- In reality the math depends highly on the application, but of course research the math behind it if it interests you.
- Step 12 Put multiple layers of software and mechanical safeties in place so if the loop were to go unstable, nothing catastrophic would occur.
Source:
This graph is adapted from a comment by @afterburn in response to this youtube video.